Originally Posted by nj85z28 View Post
you need to check the tag on the compressor to find out the amperage, which will dictate the size wire/ 2 pole breaker you need to run for your new outlet.
what he said

after than its pretty straight forward as far as the hookup, the only tricky part would be getting the wiring from point a to point b.

im pretty confident a 20 amp circuit, with #12 gauge wire would be sufficient for the app. I would really doubt it draws anymore than 8 amps at 220 volts.