Home Electrical Question
I know there are a few electricians on here so I thought I'd post up:
I have a room air conditioner that pulls 12A @ 110. I ran a dedicated outlet for it using 12ga romex (just in case) and a 15A breaker that pulls off of a 30A subpanel.
For most of the day the A/C unit runs fine, but occasionally I blow the breaker and I don't know why. The unit is only supposed to pull 12A, not enough to blow the 15A breaker. I've got a 20A breaker ready to go but I don't want to put it in if it's going to be a band aid to a bigger problem.
Any ideas?
|
|
|
07-06-2008, 02:13 PM
|
#2
|
15 Second Club
Join Date: Aug 2005
Location: Beaufort SC
Posts: 1,165
|
whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw.
__________________
2005 Colorado Z71 - Supermod tuned, SuperSparkz, Resonator delete, SuperMod PTB
next up - 3" lift, Gutted cat/retune/muffler
Past Toys:
1983 Trans AM, 1988 Trans AM, 2001 Dodge Ram 1500 Off-Road, 1986 Camaro IROC, 1984 Chevy K10 lifted, 1988 Mustang GT, 2006 Silverado 2500HD
|
|
|
07-06-2008, 02:32 PM
|
#3
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
Quote:
Originally Posted by trashman01
whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw.
|
12A.
|
|
|
07-06-2008, 02:34 PM
|
#4
|
Join Date: Jun 2007
Location: Arm pit of the world... NJ
Posts: 2,677
|
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
__________________
John
|
|
|
07-06-2008, 02:37 PM
|
#5
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
Quote:
Originally Posted by Featherburner
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
|
Yeah, I have been reading up on that. Looks like 20A will be the way to go.
|
|
|
07-06-2008, 02:41 PM
|
#6
|
Power Member
Join Date: Oct 2007
Location: Milford NJ
Posts: 1,526
|
Quote:
Originally Posted by Featherburner
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
|
exactly right.
the issue is probably this; when the air turns on the compressor starts, its a motor load and when motors start they draw and VERY large amount of current during the initial start-up, then settle back to the running load. This is why the 15A breaker trips sometimes. The 20A breaker will cause no issues, just dont overload the 30 sub-panel.
And like featherburner said, a circuit it not supposed to draw more that 80% of its ampacity on a continuous load, like an air conditioner. It can actually degrade the breaker and other components due to excessive heat.
________
Coach purses
Last edited by //<86TA>\\; 05-04-2011 at 06:51 PM.
|
|
|
07-07-2008, 04:14 PM
|
#7
|
Join Date: Feb 2005
Location: Little Egg Harbor NJ
Posts: 1,175
|
use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker.
__________________
2011 Camaro 1SS Cyber Grey Metallic
2005 Silverado
|
|
|
07-07-2008, 04:18 PM
|
#8
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
Quote:
Originally Posted by nj85z28
use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker.
|
True. I am aware of this. I didn't think I "needed" the 12 gauge wire, but I used it as overkill. Thanks though!
I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.
|
|
|
07-07-2008, 04:23 PM
|
#9
|
Join Date: Feb 2005
Location: Little Egg Harbor NJ
Posts: 1,175
|
the only thing you really use a 15 amp breaker for in a house is lighting and some light duty receptacles. at least its an easy fix and you dont have to rip the wire back out. good luck
__________________
2011 Camaro 1SS Cyber Grey Metallic
2005 Silverado
|
|
|
07-07-2008, 09:21 PM
|
#10
|
Power Member
Join Date: Oct 2007
Location: Milford NJ
Posts: 1,526
|
Quote:
Originally Posted by WildBillyT
I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.
|
like we said, 12A will not trip a breaker, but its the starting current spike of the AC that will do it. Its probably upwards of 25 amps for a split second.