Home Electrical Question

I know there are a few electricians on here so I thought I'd post up:

I have a room air conditioner that pulls 12A @ 110. I ran a dedicated outlet for it using 12ga romex (just in case) and a 15A breaker that pulls off of a 30A subpanel.

For most of the day the A/C unit runs fine, but occasionally I blow the breaker and I don't know why. The unit is only supposed to pull 12A, not enough to blow the 15A breaker. I've got a 20A breaker ready to go but I don't want to put it in if it's going to be a band aid to a bigger problem.

Any ideas?
WildBillyT is offline   Reply With Quote
Old 07-06-2008, 02:13 PM   #2
trashman01
15 Second Club
 
Join Date: Aug 2005
Location: Beaufort SC
Posts: 1,165
iTrader: (0)
whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw.
__________________
2005 Colorado Z71 - Supermod tuned, SuperSparkz, Resonator delete, SuperMod PTB

next up - 3" lift, Gutted cat/retune/muffler

Past Toys:
1983 Trans AM, 1988 Trans AM, 2001 Dodge Ram 1500 Off-Road, 1986 Camaro IROC, 1984 Chevy K10 lifted, 1988 Mustang GT, 2006 Silverado 2500HD
trashman01 is offline   Reply With Quote
Old 07-06-2008, 02:32 PM   #3
WildBillyT
Ayatollah of Rock N Rolla / Admin
 
WildBillyT's Avatar
 
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
iTrader: (10)
Quote:
Originally Posted by trashman01 View Post
whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw.
12A.
WildBillyT is offline   Reply With Quote
Old 07-06-2008, 02:34 PM   #4
Featherburner
 
Join Date: Jun 2007
Location: Arm pit of the world... NJ
Posts: 2,677
iTrader: (1)
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
__________________
John
Featherburner is offline   Reply With Quote
Old 07-06-2008, 02:37 PM   #5
WildBillyT
Ayatollah of Rock N Rolla / Admin
 
WildBillyT's Avatar
 
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
iTrader: (10)
Quote:
Originally Posted by Featherburner View Post
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
Yeah, I have been reading up on that. Looks like 20A will be the way to go.
WildBillyT is offline   Reply With Quote
Old 07-06-2008, 02:41 PM   #6
//<86TA>\\
Power Member
 
//<86TA>\\'s Avatar
 
Join Date: Oct 2007
Location: Milford NJ
Posts: 1,526
iTrader: (1)
Quote:
Originally Posted by Featherburner View Post
Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.

exactly right.

the issue is probably this; when the air turns on the compressor starts, its a motor load and when motors start they draw and VERY large amount of current during the initial start-up, then settle back to the running load. This is why the 15A breaker trips sometimes. The 20A breaker will cause no issues, just dont overload the 30 sub-panel.

And like featherburner said, a circuit it not supposed to draw more that 80% of its ampacity on a continuous load, like an air conditioner. It can actually degrade the breaker and other components due to excessive heat.
________
Coach purses

Last edited by //<86TA>\\; 05-04-2011 at 06:51 PM.
//<86TA>\\ is offline   Reply With Quote
Old 07-07-2008, 04:14 PM   #7
nj85z28
 
nj85z28's Avatar
 
Join Date: Feb 2005
Location: Little Egg Harbor NJ
Posts: 1,175
iTrader: (16)
use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker.
__________________
2011 Camaro 1SS Cyber Grey Metallic
2005 Silverado
nj85z28 is offline   Reply With Quote
Old 07-07-2008, 04:18 PM   #8
WildBillyT
Ayatollah of Rock N Rolla / Admin
 
WildBillyT's Avatar
 
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
iTrader: (10)
Quote:
Originally Posted by nj85z28 View Post
use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker.
True. I am aware of this. I didn't think I "needed" the 12 gauge wire, but I used it as overkill. Thanks though!

I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.
WildBillyT is offline   Reply With Quote
Old 07-07-2008, 04:23 PM   #9
nj85z28
 
nj85z28's Avatar
 
Join Date: Feb 2005
Location: Little Egg Harbor NJ
Posts: 1,175
iTrader: (16)
the only thing you really use a 15 amp breaker for in a house is lighting and some light duty receptacles. at least its an easy fix and you dont have to rip the wire back out. good luck
__________________
2011 Camaro 1SS Cyber Grey Metallic
2005 Silverado
nj85z28 is offline   Reply With Quote
Old 07-07-2008, 09:21 PM   #10
//<86TA>\\
Power Member
 
//<86TA>\\'s Avatar
 
Join Date: Oct 2007
Location: Milford NJ
Posts: 1,526
iTrader: (1)
Quote:
Originally Posted by WildBillyT View Post

I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.

like we said, 12A will not trip a breaker, but its the starting current spike of the AC that will do it. Its probably upwards of 25 amps for a split second.
________
Marijuana medical

Last edited by //<86TA>\\; 05-04-2011 at 06:52 PM.
//<86TA>\\ is offline   Reply With Quote
Reply

  NJFBOA - Home of New Jersey's Camaros and Firebirds > Community Forums > Lounge


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

» Sponsor List














All times are GMT -5. The time now is 05:31 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.